CompTIA Server+ SK0-005 Practice Question
During a hardware refresh, a systems administrator populates the bottom 10 U and the top 8 U of a 42 U cabinet that sits in a raised-floor cold-aisle/hot-aisle layout. All installed 1 U servers draw air in from the front and exhaust out the rear. Soon after the systems come online, temperature probes on the front of the upper servers report inlet temperatures that are 8 °C higher than those recorded at the bottom of the rack, even though the CRAC supply temperature and airflow are within specification. Which rack-level action will BEST restore proper cooling for the affected servers?
Install blanking panels in the empty rack units between the two groups of servers.
Increase the CRAC fan speed to raise static pressure in the cold aisle.
Replace the perforated rear door of the cabinet with a solid door to keep exhaust air inside the rack.
Rotate the top servers so their rear panels face the cold aisle and their fronts face the hot aisle.