A cloud provider is designing a new private data center that must meet a customer's requirement for 99.982 percent annual availability (about 1.6 hours of allowable downtime per year). The customer also mandates that every critical environmental system, including Heating, Ventilation, and Air Conditioning (HVAC), remain online even when any single component is taken out of service for maintenance. According to Uptime Institute Tier III criteria, what is the minimum HVAC redundancy configuration the data-center design must include to satisfy these requirements?

  • N (exactly the amount of cooling capacity required, with no spare components)

  • 2N (two completely independent and fully redundant cooling systems)

  • N + 1 (required capacity plus one independent spare component)

  • N + 2 (required capacity plus two independent spare components)